  • I'm after a switched fused spur with a 13a fuse right?

  • Yes. Watch out for model with a hole for a wire in the front, which you don't want.

    If it blew the fuse and tripped the RCD but not the circuit breaker it's probably a Live-to-Earth fault which is the kind of thing a failing heating element does, possibly intermittently as it heats up.