You are reading a single comment by @HeyHey and its replies. Click here to read the full conversation.
  • The most obvious problem with the consumer unit is the lid can no longer be fitted because of the larger modern breakers that have been fitted. It looks like a new earth will be needed from the gas/water entry point to the CU.

    A wiring insulation resistance test would reveal wiring condition. If you don't have any shared neutrals between circuits and the wiring is in good condition a replacement CU might be enough.

    It's not like there aren't houses all over the country running similar setups to that without a problem but you might want rcd protection for sockets etc.

About

Avatar for HeyHey @HeyHey started