• I'm pretty sure the zones ignore stud walls as the diagrams show circles through nearby walls, but perhaps a thicker wall would be fine? Might depend on which officer you get as I don't remember it being particularly detailed around treatment of corners/obstructions...

    Edit: Complete stud walls would be fine, the diagrams I was thinking of are for incomplete dividers in bathrooms (which don't really affect things). 2018 BS-7671 example attached.

  • Surely these diagrams do show that stud walls make all the difference?

    My tumble dryer and washing machine are approx where the red X is here. If there was no partition, they'd be zone 2, but they're not because it measures from the edge of the partition (minus thickness of partition), not through it


    1 Attachment