• Yeah, doesn’t surprise me regs change, but not being able to have a normal socket in zone 2 was the point I was making.

    Sounds like the deal breaker is the socket.

  • Yep, a normal socket would still need to be 3m from water sources (old reg), but a fused spur for a washing machine needs to be outside Zone 2.

    There's a not-so-good work around involving passing cable through a zone 2 wall and then mounting the switch to the other side of the stud. Not ideal!

    2018 BS-7671 for zone restrictions attached.