You are reading a single comment by @Arducius and its replies. Click here to read the full conversation.
  • I want to add some sockets to a ring main, is it better to spur off or extend the ring?

    I have reasonable access to the wiring in the loft and I can drop new cables down inside the wall to back new boxes or - probably my preference - through the ceiling (and run cable through surface mounted conduit) from there to pattress boxes.
    Spurring off would use slightly less cable and fewer connections in total but is there anything else to consider (apart from total potential load on the circuit)?

  • You can only spur once. If you extend the ring you can then spur from that later if you want.

    It's preferred that you make connections in existing backboxes rather than just splicing into the ring under floors or in the loft etc. It's just a question of convenience in the future if someone is working on the circuit or fault finding. You have to balance that with convenience now of course!

About

Avatar for Arducius @Arducius started