  • Cheers. Switching the single socket for a double seems sensible then. It's for a washer/dryer (2.2kw) and microwave (1.3kw).

  • Quite possibly on a ring main protected by a 32amp breaker if it's in a kitchen. A ring main consists of 2 twin & earth cables (usually 2.5) which gives the cables a higher capacity due to ohms law etc...

    The total max load in your case is 3.5kw/240v=14.5A

    That probably falls within safe limits based on diversity and over engineering. The cable and breaker are likely rated for at least 16A, sockets 13A draw in each 'gang'.

  • Makes sense, although a bit of further investigation suggests that this is a spur. I guess maybe I should check the thickness of the wire