  • How about in turns of amps? Is a double socket limited to 13A between the two or 13A each?

  • A circuit wired single 2.5 twin and earth clipped in open air will have a fuse lower than 16amps is a rough rule of thumb. That is the cable will not catch fire with a 16amp draw. The cable is always the part that needs protection. The sockets are rated for 13amp draw, on a ring circuit that should include both sockets operating at 13amps otherwise it couldn't be 13amp rated.

    2 3000w appliances running full pelt is pretty unusual these days.

  • Cheers. Switching the single socket for a double seems sensible then. It's for a washer/dryer (2.2kw) and microwave (1.3kw).