Electricians, can you help explain calculating PFC? It seems to keep popping up as I need to use it to confirm the size of the CPC with the adiabatic equation.
I thought PFC = U/Zs, but with the examples we've been given, the answers are a bit different.
Also, when we did testing, PFC was either PEFC or PSC - whichever was higher. When you're designing, are you just working off PEFC as it's the CPC size I'm trying to confirm?
Say you have a building with 3 phase coming to a DB, which supplies a second 3 phase DB, which supplies a single phase DB - how do I go about calculating PFC at the single phase DB at the end?
EG:
3 Phase DB (A)--------3 Phase DB (B)------Single Phase DB (C)----
Zs@DB=0.09, 0.11, ?
PFC=5kA, 3.7kA, ?
I'm selecting equipment for a planned extension, so all the values for the single phase DB (C) and it's supply etc will be based off calculation.
Electricians, can you help explain calculating PFC? It seems to keep popping up as I need to use it to confirm the size of the CPC with the adiabatic equation.
I thought PFC = U/Zs, but with the examples we've been given, the answers are a bit different.
Also, when we did testing, PFC was either PEFC or PSC - whichever was higher. When you're designing, are you just working off PEFC as it's the CPC size I'm trying to confirm?
Say you have a building with 3 phase coming to a DB, which supplies a second 3 phase DB, which supplies a single phase DB - how do I go about calculating PFC at the single phase DB at the end?
EG:
3 Phase DB (A)--------3 Phase DB (B)------Single Phase DB (C)----
Zs@DB=0.09, 0.11, ?
PFC=5kA, 3.7kA, ?
I'm selecting equipment for a planned extension, so all the values for the single phase DB (C) and it's supply etc will be based off calculation.