  • You need to have the extension kit for the TRVs though - otherwise they won't call the boiler.

    They'd just open & close the radiators, and only when the boiler is on (via another programmer I guess) would they heat up. Worse - if they are closed, and the boiler is on, you'd be circulating and heating water through a tiny loop.

  • Worse - if they are closed, and the boiler is on, you'd be circulating and heating water through a tiny loop.

    That shouldn't be a big problem. You should always have one radiator without a TRV and the water in the short loop will rapidly reach the boiler set temp which will then switch off the burny bit.