Makes sense, I think. Are we basically saying the cable is probably fucked somewhere in the run? I’m not sure what the size is but it’s heavy twin & earth and the main conductors only just fit into socket terminals. Chased into the wall behind tiles (which is where a popping noise comes from when the MCB trips).
If the earth is broken somewhere its apparent voltage will free float. If there's also a high resistance fault to live its measured voltage will become that of live. Whereas continuity will only buzz if there's a low resistance between the conductors.