    And as a follow-up, is there any knock on implications for the plug and socket for the lead?

    Cheers.

  • is there any issue with overspecing the lead by using 2.5mm² 3 Core?

    Not really but it can be a bit of a sod fitting the cable into 13A plugs and extension sockets. I'd just stick with 1.5mm cable personally as the voltage drop isn't likely to be an issue.