Also, niche sparky question.
When you’re doing diversity calculations for your consumer box ratings (I’ve probably described that wrong). In the on site guide, it says 10a + 30% i.f. + 5a if socketed for cookers.
Say your total max current is 80a, would you do:
10a + 30% of 70a +5a
Or 30% of 80a + 10a + 5a
My understanding is that it’s the former - 100% of 10a, 30% of the remainder, + 5a for the socket. But it’s not totally clear.