  • Rad in the hallway isn't hearing up.
    All other rads on. Thermostatic valve set to max. All radiators fitted a month ago. There isn't any air in the radiator.

    Suggestions?

  • Mate had a similar problem recently.

    Bled the (small amount of) air.
    No change.

    Checked the valve on the other end of the radiator.
    Inexplicably it was locked shut/off.

    Opened it up, radiator became instantly warm at the inlet,
    and whole radiator too hot to touch within minutes.

  • Turn down the thermostatic valves on the other radiators and see if it heats up then. Sometimes you need to balance the flow otherwise radiators get starved. It's a common problem in shared houses where people turn up their own radiators and one or 2 rooms end up without any heat. I'm not very good at balancing them but I've seen plumbers do it to whole houses.

  • Has the radiator just stopped working or have you just noticed? Is it only one rad or could it on a separate heating zone within the boiler...
    Is it on the end of the pipe run?
    Turning the others off is deffo the quickest way to check flow, balancing them is a case of narrowing the rad valves closest to the boiler and gradually having them more open the further down the pipe loop.