  • All the sockets are working....That is strange.

    I'd check the fuseboard/consumer unit and see if the wire has become disconnected.

  • Yeah it's bizarre. Ground floor and loft work (though I found that the loft sockets are actually marked as 'Water Heater' on the consumer board), along wiht everything else in the house.

    It's a modern board, so MCBs rather than fuses. I've now re-attached the old socket in case there was a fault but still no dice. I think it's time amateur hour came to an end and I called a pro.

  • Surely the ground floor and loft work on separate rings.

    Pop that single socket off again (with the mains isolated on the MCB) and check that the incoming and outgoing cables are securely screwed in.