Ok. To start. As a sparkie [...]
@well_is_it Ignore this chancer. You will have to rewire because when you sell the same questions you asked will be asked again.
A sparkie.
Scaremongering.
Telling someone they need a rewire.
Quel. Fucking. Surprise.
(FWIW I do agree that the electrics want looking at. I would, as I said, be contemplating lumping a rewire in with other work to minimise disruption. But your bald, unqualified statement that @well_is_it should "Avoid" is pure and simple bollocks.)
Ok. To start. As a sparkie I'm well aware that previous work doesn't have conform to modern regulations but as you get further away from the 1970's (which is when that would've compiled) it gets harder to justify. You are aware that the recent 17th edition update now recommends all metal consumer units? And RCD protection in domestic installs is a life saver, especially in 'special locations' such as bathrooms and external power.
RCD's don't trip in the way that fuses or mcb's do. They sense current loss that would not trip a fuse and will fault within 40ms at 30mA.
Fuses, especially rewirable links, do not offer the same protection.
The fact that I mentioned a rewire is that with consumer unit in that state will imply that the wiring is in bad shape also. Shared neutrals, green goo from old PVC T&E and unsheathed earths are a high probability, the electrics need checking. Also the fact that modern houses and equipment put a higher load and strain on the elctrical systems than they did 40 years ago.
Of course. Thats what any self respecting qualified electrician would recommend.
@well_is_it Ignore this chancer. You will have to rewire because when you sell the same questions you asked will be asked again.